Wrong calculation of "Power House Load Yield" #68
Unanswered
cmovetus75
asked this question in
Question / Answer
Replies: 1 comment 2 replies
-
I remember playing around with the formulas when Forced Charge first was introduced. My conclusion back then was to leave things as they were. What do you base your assumption on - that all PV Yield is sent to the battery in Forced Charge? It would make sense from a "efficiency" POV if the system behaves like you describe. But if you make the changes you suggest you increase the house load consumption from grid and improve the battery economy - I think it is debatable if that is the "correct" way. I'll have a look at it. |
Beta Was this translation helpful? Give feedback.
2 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
-
After installing the package with the PEES sensors everything has worked fine except the calculation of "Power House Load Yield" (sensor.power_house_load) and all sensors that further use this value and associated utility meters under some circumstances.
In particular, in forced charge and forced discharge modes of use of the battery, the formula used in the template sensor to calculate the load of the house that is being sourced from PV Panels (Power House Load Yield) does not cover properly this use case.
The current pseudo formula is more or less :
If (House Load > PV Yield) then House Load Yield = PV Yield
Else House Load Yield = House Load
If in forced charge mode, all PV Yield is sent to the Battery (for later use when the electricity cost is more expensive), but with the above formula would assume that the PV Yield is being sent to the House Load.
I have being using for some hours a new formulation that seems to be working well. I have identified 4 different scenarios, that require a diferent formula according to the power flow diagram:
If (batteries_charge_discharge_power > 0) (charging)
If PV Yield > Charge -> House Load Yield = House Load – Import
If PV Yield ≤ Charge -> House Load Yield = 0
Else (discharging)
If Discharge < Load -> House Load Yield = PV Yield – Export
If Discharge ≥ Load -> House Load Yield = 0
I have attached the modified PEES yaml definition that I am currently using.
huawei_solar_pees (Power House Load Yield corrected).txt